Status
Not open for further replies.

Mike01

Senior Member
Location
MidWest
I am trying to find a certain fitting and am not sure if it is available I want to transition from 1/2" RGS to Liquid tight flexible conduit but have not been able to locate the appropriate fitting?
 

nez

Member
Most people would just use a threaded rigid coupling and thread the liquidtight connector into the rigid coupling. You could also transition with a junction box.
 

S'mise

Senior Member
Location
Michigan
Most people would just use a threaded rigid coupling and thread the liquidtight connector into the rigid coupling. You could also transition with a junction box.

Some say its a violation 300.15(F) because it's not listed. It's cool with me but I'm not the AHJ
 