cable connection to switchgear

Status
Not open for further replies.
when using tc cable in a cable tray and entering an indoor switchgear enclosure, is a strain relief connector required on the cable? can a chase nipple be used?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Welcome to the Forum

I know of no requirement for a strain relief connector.
Note the 6 ft limitation in 336.10(7) if the tray is not continuous.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Good point, Don. I will have to say that in the TC installs I have seen that has been pretty much totally ignored :) perhaps thru ignorance as in my part, or by design...plus I imagine connectors for a 500 kmil 3 conductor tray cable are hard to come by.
75% of the CT/switchboard installs I have seen have nothing but an opening in the cabinet.
You would think there would be an exeption, especially for large cables, but I have found none.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
We don't use much tray cable, but on the jobs were we have used it, I had no problems getting connectors for it, and some of was 3c, 500kcmil.
 