Depending upon what type of meter you are using to mesure this with, 129 volts is high, but not to the point it should be causing this amount of failure, since your 208 is also high, this has to be a problem with the transformer or ahead of it.
I would expect a hospital to be fed with a 480/277 system, then have many 480-208/120v transformers for local loads, if so you need to see what the 480 voltage is, if its high also then the POCO needs to be brought into the problem, if the POCO supplys the 208/120 then same thing, otherwise the hospital owns the transformers, and someone is going to need to trouble shoot where the hi voltage starts.
High voltage on the secondary is only caused by a few things:
Shorted primary turns.
Too low primary tap setting.
If Y supply, lost Y neutral with transformer fed line to neutral. (single phase)
Higher then normal primary voltage.