I recentley had an installation for exterior low votage lighting. Using step down transformers that came with a cord and cap to plug into an outlet. I removed the cord cap and wired it directly, using a strain relief connector in the box and to a switch as a means of disconnect. The inspector turned it down citing it was against the code to connect SO cord to a switch. He did not refer to a certain section of the code. Is there anything in the code (2008) against the type of installation?
 
I think i found it

I think i found it

In article 400, 400.7A lists uses permitted and 400.7B states the cord must equipped with an attachment plug and shall be energized from a receptacle outlet
 

jumper

Senior Member
In article 400, 400.7A lists uses permitted and 400.7B states the cord must equipped with an attachment plug and shall be energized from a receptacle outlet