5-53 Log #1857 NEC-P05 Final Action: Reject
(250.2)
____________________________________________________________
Submitter: XXXXXXXXXXX, XXX., Santa Fe, NM
Recommendation: Add new text to 250.2 to read as follows:
Objectionable Current. Current that flows through paths other than the
intended grounded circuit conductors during normal operation of a system.
Substantiation: Objectionable current is not defined in the NEC. ANSI/IEEE
std 446-1987 has interpreted objectionable current, and states the following:
That neutral currents that flow through paths other than the intended
grounded (neutral) circuit conductors during normal operation of a system will
be deemed objectionable if they contribute to any of the following:
(1) Interference with the proper operation of equipment, devices, or systems
that are sensitive to electromagnetic interference, such as electronic equipment,
communications systems, computer systems, etc.
(2) Interference with the proper sensing and operation of ground-fault
protection equipment.
(3) Arcing of sufficient energy to ignite flammable materials.
(4) Detonation of explosives during production, storage, or testing.
(5) Overheating due to heat generated in raceways, etc., as a result of stray
current.
Panel Meeting Action: Reject
Panel Statement: The proposed definition does not match and is not
supported by the submitter’s substantiation. The definition is not appropriate,
since it is not always feasible to avoid some current flow due to inductive and
capacitive coupling within equipment and wiring systems.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15