Does 110.26(A)(1) apply to a motor disconnect if I can lock out a controller

Status
Not open for further replies.
Does 110.26(A)(1) apply to a motor disconnect if I can lock out a controller which feeds the disconnect prior to opening the safety switch/disconnect? The controller is designed to be locked out and isolates all power sources to the disconnect.
 

tom baker

First Chief Moderator
Staff member
Yes and no. See section (B). Most of the time you will need a disconnect within sight of the motor. Submersibles and industrial locations are examples where the controller can serve as the disconnect.
 