Hi all -thanks for any input...
Changing a 240V cooktop, calls for 40 amp circuit, manual instructs special procedures if supply is also aluminum (such as copper pigtail between ALs). I have #6 AL SE XHHW to jb for old stove - no problem with ampacity.
The cooktop comes with 6 feet of #10 aluminum XLPE (seems OK for OEM), with about 50 strands (in FMC). As I read, I seem to crossed a flexible conductor limit. But my supply guys act like I'm the only one ever to ask for flex, dual rated connectors.
Am I researching this right, or have I overlooked something obvious? Am I making this too complicated? Would split bolts (Al/Al type) inherently be flex rated? Is that flex rating only for screw and crimp types connectors or for all? What's really different physically in a flex connector?
I wonder because the listed device does call for special connections because of Al/Al hazard, but never mentions the high flexibility of the conductor as a special consideration.
Another thing that bothers me is that the FMC on the cooktop came with nice, neat rubberized cloth tape around the conductors (as though for neatness), and then explictily covering the end of the FMC where it would go into a flex connector for about 2 inches - as though to prevent any grounding to the connector at the box.
I have cut through the tape for flex connector continuity, and used the old purple CU/AL wirenuts as I look for the right or best connectors.
Any help?
Changing a 240V cooktop, calls for 40 amp circuit, manual instructs special procedures if supply is also aluminum (such as copper pigtail between ALs). I have #6 AL SE XHHW to jb for old stove - no problem with ampacity.
The cooktop comes with 6 feet of #10 aluminum XLPE (seems OK for OEM), with about 50 strands (in FMC). As I read, I seem to crossed a flexible conductor limit. But my supply guys act like I'm the only one ever to ask for flex, dual rated connectors.
Am I researching this right, or have I overlooked something obvious? Am I making this too complicated? Would split bolts (Al/Al type) inherently be flex rated? Is that flex rating only for screw and crimp types connectors or for all? What's really different physically in a flex connector?
I wonder because the listed device does call for special connections because of Al/Al hazard, but never mentions the high flexibility of the conductor as a special consideration.
Another thing that bothers me is that the FMC on the cooktop came with nice, neat rubberized cloth tape around the conductors (as though for neatness), and then explictily covering the end of the FMC where it would go into a flex connector for about 2 inches - as though to prevent any grounding to the connector at the box.
I have cut through the tape for flex connector continuity, and used the old purple CU/AL wirenuts as I look for the right or best connectors.
Any help?