breaker size for sub panel

Status
Not open for further replies.

tmason

Member
i have a sub panel square d homeline 100 amp if i run number 4 thhn wire rated at 90 c what size breaker would i need
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
i have a sub panel square d homeline 100 amp if i run number 4 thhn wire rated at 90 c what size breaker would i need

Assuming this is not nm cable or se cable and the feeder does not carry the entire load of the dwelling- if it is a dwelling then I would say 90 amps if the calculated load is 85 amps or less. 240.4(B)
 