jusme123

Senior Member
Location
NY
Occupation
JW
When terminating switch gear (bottom fed), is it permissible to take the grounds inside the conduits directly to the ground bus (bypassing grounding bushing), and than run one ground wire from the ground bus to all the grounding bushings on the conduits. Code section would be appreciated! Thanks
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
You would have to size the single EG back to the conduits for the max OCPD. Maybe a 4/0 vs 12s.

I do not believe this method is prohibited, so there will be no NEC reference to allow it.

Won't be the first time I am wrong, so just wait a bit.

Are these Service Entrance conductors or feeder and branch circuits?
 

tkb

Senior Member
Location
MA
I don't see a problem with it.
I have seen it many, many times.
Seems like it would be the same as if they were terminated through a KO.
 

RUWired

Senior Member
Location
Pa.
Whether it is a service or feeder the conduits are bonded with either method.

The size of the bonding jumper is what would matter. With service conductors the jumper is sized per 250.66 and feeder bonding jumpers would be sized per 250.122.

Rick
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If it's a service, you may create a problem. A single bonding jumper would need to be sized to the sum of the area of the service conductors {250.102(C)} and you could end up with a conductor so large as to require upsized of lugs, etc.
With individual bonds they only need to be sized to the conductor in the one conduit they bond.

On feeders the jumper would be sized by the largest OCP device so there is no normally a problem using just one jumper.
 

jusme123

Senior Member
Location
NY
Occupation
JW
If it's a service, you may create a problem. A single bonding jumper would need to be sized to the sum of the area of the service conductors {250.102(C)} and you could end up with a conductor so large as to require upsized of lugs, etc.
With individual bonds they only need to be sized to the conductor in the one conduit they bond.

On feeders the jumper would be sized by the largest OCP device so there is no normally a problem using just one jumper.
Augie, my stance is that the ground in the conduit is to be connected to the grounding bushing and than continue to the ground bus
 

tkb

Senior Member
Location
MA
If it's a service, you may create a problem. A single bonding jumper would need to be sized to the sum of the area of the service conductors {250.102(C)} and you could end up with a conductor so large as to require upsized of lugs, etc.
With individual bonds they only need to be sized to the conductor in the one conduit they bond.

On feeders the jumper would be sized by the largest OCP device so there is no normally a problem using just one jumper.

So that would be 3/0 for a service and 250 for a feeder.

Augie, my stance is that the ground in the conduit is to be connected to the grounding bushing and than continue to the ground bus

Based on...
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
So that would be 3/0 for a service and 250 for a feeder.

...

As I read it, if he had an 1800 amp service composed of (5) conduits with 500 kcmil, he could run a 3/0 to each conduit, or if he chose to run only 1 jumper for all it would nedd to be 350 kcmil (12.5% of total).


For an 1800 amp feeder it would be a 250 kmil to each or to all.
 

tkb

Senior Member
Location
MA
As I read it, if he had an 1800 amp service composed of (5) conduits with 500 kcmil, he could run a 3/0 to each conduit, or if he chose to run only 1 jumper for all it would nedd to be 350 kcmil (12.5% of total).


For an 1800 amp feeder it would be a 250 kmil to each or to all.

Opps...I didn't read the note under the table.
 