List of used 3-phase voltages from 400V - 2400V

Status
Not open for further replies.

jtrezon

Member
Looking for a list of all used/known 3-phase industrial voltages from 400V - 2400V
3W, 4W, 50-60Hz, Wye, Delta....all of the above.
 

Besoeker

Senior Member
Location
UK
Looking for a list of all used/known 3-phase industrial voltages from 400V - 2400V
3W, 4W, 50-60Hz, Wye, Delta....all of the above.

For industrial use in un UK it is usually 400V, 3.3kV, 6.6kV, and 11kV.
I have seen equipment like arc furnaces that are fed from the grid at 132kV.
It is becoming increasingly common to use 690V for larger variable speed drives but it isn't a standard voltage and usually has to be derived locally.
 

robbietan

Senior Member
Location
Antipolo City
Looking for a list of all used/known 3-phase industrial voltages from 400V - 2400V
3W, 4W, 50-60Hz, Wye, Delta....all of the above.

transformers commonly provided by the poco here have a 34.5 kV wye primary and a delta secondary at 480V. the taps of the transformer can accomodate a +/- 12% bandwith, which can cover voltages of 440 and 460 V

other service voltages available are 400V, 115kV, 13.8 kV (line to line) and 69kV in very few areas
 

broadgage

Senior Member
Location
London, England
The uncommon UK voltage of 690 reffered to above is sometimes used for large scale lighting.
The larger HID ballasts are designed for 400 volts nominal and normally connected between phases of a 230/400 volt system. They may also be used between phase and neutral on a 400/690 volt system.

Railway signalling power is sometimes distributed at 660 or 690 volts and transformed down to 24 or 110 volts at the point of use.
 

jtrezon

Member
Clarification....

Clarification....

Researching for a facility that will assemble and test generators. Because they ciuld end up anywhere in the world, I am looking for all know industrial applications, 3-ph, 400V to 2.4kV only. Anyone know of any others?
400V
415V
440V
460V
480V
500V
550V
575V
600V
690V
?
?
?
2.4kV
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Before you expend resources for all of these different voltages, you need to investigate the differences between "Utilization Voltage" and "Distribution / Generation Voltage". Basically Utiliz. Voltage is what motors and other equipment is built to, Dist. / Gen. Voltage is what utilities supply. The reason for the difference is to accommodate voltage drop at the point of use. So for example in the US, 480V is what is distributed, 460V is what the motors are designed for.

Researching for a facility that will assemble and test generators. Because they could end up anywhere in the world, I am looking for all know industrial applications, 3-ph, 400V to 2.4kV only. Anyone know of any others?
400V - 50Hz only
415V - 50Hz only
440V - Legacy utilization, now 460V
460V - Utilization, not generation
480V - 60Hz only
500V - Extremely rare
550V - Rare/old
575V - Utilization, not generation
600V - 60Hz only
690V
1000V - Mining machinery only
1500V - Mining machinery only
?
2.4kV
 