I have a 20HP 230v 3phase motor on a Portable Chop Saw. Table 430.250 says to use 54A.
Using table 400.5 Column A would a #4 be correct for wiring a 20hp chop saw. This saw is on a rolling platform to be able to move around to keep from having to lift these wire ropes very high off the floor to be able to cut them. Was going to run this SO cord from a 100A Non fused disconnect. Ckt is being fed from a breaker in a panel sized per 430-52. Is this a installation code compliant.
thanks
I have a 230v - 3phase - 20HP Wire rope Saw, that is mounted on its own platform with wheels to be able to roll around close to floor to have from having to lift the cable up very high to cut it off. I am looking for some help in wiring this equipment. If you use table 430-250 for a 20hp = 54A.
54A x 125% = 67.5A I will have to use a #4 thhn Branch circuit conductor per 430-250 and
54A x 250% = 135A I will have to use a 150A Breaker per 430-6 & 430-52
Customer wants this wired with a receptacle a SO type installation so to have a little portablitiy.
54A x 125% = 67.5A Need a #2 Type SO per 400-5
The total distance from Panel to receptacle is 115'
Distance from receptacle to saw (30' of SO cord)
If this is correct sizes of conductors and breakers, What type and size of receptacle could be used . Also the problem I have had in the past is the conductors are usually to big to land in the controller of the equipment.
Thanks
Using table 400.5 Column A would a #4 be correct for wiring a 20hp chop saw. This saw is on a rolling platform to be able to move around to keep from having to lift these wire ropes very high off the floor to be able to cut them. Was going to run this SO cord from a 100A Non fused disconnect. Ckt is being fed from a breaker in a panel sized per 430-52. Is this a installation code compliant.
thanks
I have a 230v - 3phase - 20HP Wire rope Saw, that is mounted on its own platform with wheels to be able to roll around close to floor to have from having to lift the cable up very high to cut it off. I am looking for some help in wiring this equipment. If you use table 430-250 for a 20hp = 54A.
54A x 125% = 67.5A I will have to use a #4 thhn Branch circuit conductor per 430-250 and
54A x 250% = 135A I will have to use a 150A Breaker per 430-6 & 430-52
Customer wants this wired with a receptacle a SO type installation so to have a little portablitiy.
54A x 125% = 67.5A Need a #2 Type SO per 400-5
The total distance from Panel to receptacle is 115'
Distance from receptacle to saw (30' of SO cord)
If this is correct sizes of conductors and breakers, What type and size of receptacle could be used . Also the problem I have had in the past is the conductors are usually to big to land in the controller of the equipment.
Thanks