My way fed the wire with a more or less constant current.110305-1511 EST
G._S._Ohm:
One way to measure temperature rise of wire is to use the change of resistance of copper with respect to temperature. This technique is also useful to measure average internal temperature rise in a transformer.
For your #14 Romex experiment a 250 ft length will provide enough resistance to allow moderately accurate resistance measurements. Use both wires in the Romex to generate heat, but use only one for the resistance measurement. Make the one wire a 4 terminal resistor to get accurate resistance measurements. #14 copper is about 2.525 ohms per 1000 ft. So 250 ft is about 0.631 ohms. For annealed copper the coefficient at 20 deg C is 0.00393 and 0.00382 for hard drawn copper. For a 10% change in resistance the temperature rise is about 0.1/0.00393 = 25.4 deg C. This is a wire temperature of 114 deg F. for room ambient of 20 deg C.
I seriously doubt that you only had a 2 deg C wire temperature rise in your experiment.
.
Try it. I can always use experimental corroboration - or lack of it. I used a precision thermistor to measure the temp. under the jacket.
Another way is to use one of the Weller soldering guns with the two posts. They put out about 150 A into the tip @ 1 or 2 vac so with a few feet of Romex you can drop the current down to 30 A or so.
The next thing I want to do is put a few amps of DC into cable armor. Along with the AC impedance this should give the inductance per foot of this coiled shield.