Code disagreement on AFCI with Inspector

Status
Not open for further replies.

Dave R

New member
According to Article 210-12 are lighting outlets required to be protected or just receptacle outlets?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
The text of the code article just says "outlets." That would include any and all types (i.e., receptacles, lights, smoke alarms).
 

al hildenbrand

Senior Member
Location
Minnesota
Occupation
Electrical Contractor, Electrical Consultant, Electrical Engineer
Yes, lights, smoke alarms, fans and receptacles unless you are still on the 1999 NEC
Yes.

And, even a 15 or 20 amp 120 Volt hard wired something or other.

"Outlet" is a very broad term. Look at its definition in Article 100 Definitions.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
According to Article 210-12 are lighting outlets required to be protected or just receptacle outlets?

I beleive FL is under the 2008 NEC and with your use of the dash it appears you are using 99 or earlier code book, the inspector should be requiring all 120 volt 15 and 20 amp branch circuits supplying outlets (with a few exceptions) to be AFCI protected.

From the 2008 NEC

(B) Dwelling Units. All 120-volt, single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, or similar rooms or areas shall be protected by a listed arc-fault circuit interrupter, combination-type, installed to provide protection of the branch circuit.

Roger
 

pete m.

Senior Member
Location
Ohio
Just for the sake of discussion, if a jurisdiction were still enforcing the 99 NEC wouldn't the arc fault requirement be in effect for bedrooms due to the last sentence of 210-12(B)?

Pete
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Just for the sake of discussion, if a jurisdiction were still enforcing the 99 NEC wouldn't the arc fault requirement be in effect for bedrooms due to the last sentence of 210-12(B)?

Pete

Yes.

Roger
 

construct

Senior Member
Just for the sake of discussion, if a jurisdiction were still enforcing the 99 NEC wouldn't the arc fault requirement be in effect for bedrooms due to the last sentence of 210-12(B)?

Pete

In the 99 NEC 210-12 (b) says "all branch circuits that supply 15- and 20-ampere receptacle outlets (not all outlets in bedrooms). :roll:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
In the 99 NEC 210-12 (b) says "all branch circuits that supply 15- and 20-ampere receptacle outlets (not all outlets in bedrooms). :roll:
I think by Pete referencing the 1999 requirement that is exactly what he said.

Roger
 