Type AC cable vs FMC

Status
Not open for further replies.

VIC1958

Senior Member
Is a seperate grounding conductor needed on both of these or is the outside metal sheathing considered the grounding conductor? Does the mfg have to state somewhere on the package that the outside sheathing is an acceptable grounding conductor?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
320.108 provides that AC shall be provide a adequate ground path.
348.60 for FMC references you back to 250.118(5) which places limitations on FMC's ground path including a 6 ft limit, as rcarroll notes
 
Status
Not open for further replies.