Dining room AFCI requirements

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
210.52B requires the dining room receptacles to be on the small appliance branch circuit. 210.12B requires dining room receptacles to be AFCI protected.
Am I reading this correctly and how are people dealing with this?
:confused:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
210.52B requires the dining room receptacles to be on the small appliance branch circuit. 210.12B requires dining room receptacles to be AFCI protected.
Am I reading this correctly and how are people dealing with this?
:confused:

Yep, I just run a separate circuit to the dining room as I don't want the kitchen counter on AFCI
 