We have a large campus power system that consists of 3 substation transformers that are considered the service point of the system. Primary line voltage is 34.5kv and is transformed down to 4160v and distributed to many 4160/480 volt outdoor transformers with adjacent load centers. These transformers range from 500 to 1500 KVA wye/ wye connected with HO and XO ungrounded (floating). From these load centers, feeders are brought into various buildings such as office, warehouses and vehicle maintenance buildings. The load centers have ground fault light indication.
I understand that this installation does not meet the requirements of 250.20, 250.21… We are trying to remedy the issue and I am looking for help. The wiring method from the load center is RGC with three phase conductors and no neutral and no EGC, We derive a neutral from a transformer inside the building to pick up 277 volt loads where needed. Article 250.97 is followed, for the most part, for the grounding and bonding part of things. Panels inside the buildings are 30 plus years old and need of some upgrading, which leads me to a question on 250.24c. My understanding is that a neutral conductor has to be run with the phase conductors and terminated with the service equipment with the main bonding jumper even if the neutral conductor is not used. This is for services, does this apply to feeders. Next question is how unsafe ungrounded systems really are? Is there a shock hazard when equipment becomes unintentionally grounded? I have read and understand what can happen when one of the other phases starts to fault are or does fault. Any help from the experts would be greatly appreciated on this fixing this installation.
I understand that this installation does not meet the requirements of 250.20, 250.21… We are trying to remedy the issue and I am looking for help. The wiring method from the load center is RGC with three phase conductors and no neutral and no EGC, We derive a neutral from a transformer inside the building to pick up 277 volt loads where needed. Article 250.97 is followed, for the most part, for the grounding and bonding part of things. Panels inside the buildings are 30 plus years old and need of some upgrading, which leads me to a question on 250.24c. My understanding is that a neutral conductor has to be run with the phase conductors and terminated with the service equipment with the main bonding jumper even if the neutral conductor is not used. This is for services, does this apply to feeders. Next question is how unsafe ungrounded systems really are? Is there a shock hazard when equipment becomes unintentionally grounded? I have read and understand what can happen when one of the other phases starts to fault are or does fault. Any help from the experts would be greatly appreciated on this fixing this installation.
Last edited by a moderator: