From the 2001 ROP
2-151-(210-50): Reject
SUBMITTER: Edward J. Fox, Jr., Orange County Bldg Div., FL
RECOMMENDATION: 210-50: There shall be a minimum of two (2) duplex receptacles in each office, and classroom. They shall be separated by a reasonable distance to provide access from different areas of the room.
SUBSTANTIATION: By providing receptacles that would normally not be installed for offices, and classrooms, the citizens would not have to use extension cords, nor would they have to hire an electrician to come in and add receptacles after they have taken occupancy.
All offices have many electrical appliances and it would be safer if these had receptacles to plug into instead of extension cords. By providing a better electrical system up front, the citizens are not impacted by additional cost later due to adding more receptacles and circuits to handle an ever-increasing demand.
PANEL ACTION: Reject.
PANEL STATEMENT: The submitter's proposed revision does not resolve the situation presented in the substantiation. The present code rule in 210-50(b) requires a receptacle where cord and plug connections are used. Adding a rule to provide two receptacles would not keep (or in some cases even minimize) the user from violating the Code and using an extension cord, since the final usage of the particular space is not known. For non-dwelling unit applications, proper planning and design must be used to provide adequate access to receptacle outlets. If the receptacles are not provided, then it would be necessary to have receptacles installed by a qualified person.