I am bidding a set of plans that show the main electrical panel at a detached garage and guest house. This building is closest to utility pole.
The main house is quite large, it requires more than a 200 amp sub panel.
Typical equipment: Siemens 400 amp meter panel which has one 200 amp breaker with 30 spaces, and a 200 amp breaker for a sub panel.
As far as I am aware, all feeders to the main house have to be in the same conduit; I cannot run a 200 amp underground feed, and then also a 100 amp underground feed.
Should I install a 400 amp meter at garage, then a 400 amp disconnect at the main house with (2) sub panels, and then backfeed the garage with a 100 amp sub panel?
Has anyone had experience with the meter main being installed at a smaller outbuilding?
Thanks