What are my NEC compliant options

Status
Not open for further replies.
I have a 3 phase 240 volt 3-wire delta system with no neutral or ungrounded conductor going to a 100AMP MB Square D QO panel at a pumping station that feeds two 10HP submersable pumps on VFD's. I need a neutral for 120 volts to feed PLC's, lights, outlets and instruments like ultra sonic level, mag meters and floats. Are my only options to come off of 3 phase panel to a transformer then to a lighting panel or am I not looking at the big picture.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think you meant "grounded" conductor but, is it not possible to use a small transformer fed from the Delta to derive the 120?

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Is that my only option our is there a way to get a neutral with out adding a transformer

Have you questioned the POCO as to whether they could provide you with a center grounded winding off of the Delta?

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Then you have no option except to come up with your own 120 volt source and I would use a transformer as I mentioned above.

Roger
 