Grounding

Status
Not open for further replies.

erickench

Senior Member
Location
Brooklyn, NY
Hi Guys, okay I came across a very interesting multiple choice question in my passbook about grounding. Here it is:

With regard to the grounding of electrical systems, it is CORRECT to state that electrical systems

A. must always be grounded
B. must be provided with a ground detector, if ungrounded
C. must always have a separate grounding conductor
D. of less than fifty volts need not be grounded

I would have thought 'B' would be the answer because the definition of 'Grounding Conductor" in article 100 is: A conductor used to connect equipment or the grounded circuit of a wiring system to a grounding electrode or electrodes. An ungrounded system has an electrode and the definition say's nothing about connecting a grounding conductor to the service neutral. What do you guys think?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
without a voltage mentioned, I'm stuck with "none of the above" so I must be overlooking something.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The use of the term grounding has changed because of this issue. A separate grounding system can be many things. I assume they mean an EGC but an ungrounded system does not use an egc....Oh well.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Preparing question can be a difficult task.
It seems simple until you take into account all the possible variables, exceptions, etc.
 

erickench

Senior Member
Location
Brooklyn, NY
The use of the term grounding has changed because of this issue. A separate grounding system can be many things. I assume they mean an EGC but an ungrounded system does not use an egc....Oh well.

I think you would have to look at the present definition of 'Grounding Conductor'. All it say's is that the system is connected to the grounding electrode through this grounding conductor. I would assume that all non-current carrying metal parts of an ungrounded system would have to be bonded together and then connected to a grounding electrode.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If a person is not able to do as you say, they are not fit to author test questions.

So in your opinion, an author that has penned say 10,000 questions that the answers can not be disputed is not fit if he/she had one question that might possibly be incorrect.

Boy, that puts a lot of pressure on an electrician that has done 10,000 service calls without a mistake then all of a sudden..........., I shutter to think of the sense of failure and the humility when the realization of the unfitness becomes apparent to this electrician. ;););)


Roger
 

cadpoint

Senior Member
Location
Durham, NC
Just reading it as a layman (if I may) my thoughts were they are all right! :cool:

No one's going to support "A", all the other's have been called out!

One can only say "yes" something's going to happen due to the type of circuit or service to be addressed with active Code participation.

I was reading for multiply choices...
 