Do tables 310.16, 310.17, ... regarding current/wire size apply to AC and DC current? Is it permissable to use standard 20 amp AC circuit breakers for DC as well?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
You have to look at the manufactures ratings as far as using a standard breaker on DC. For example most Square D QO breakers can be used on 48 vdc systems.
 