Voltage Drop Percentage
laketime
What is a good percentage to keep voltage drop below? Also what would you calculate the load at for a quad receptacle fed by a 120/v 20amp circuit?
jumper
Except for a few applications, fire pumps and sensitive electronic equipment, voltage drop is not an NEC concern. You could use the FPN in 210.19 as guide.
FPN No. 4: Conductors for branch circuits as defined in
Article 100, sized to prevent a voltage drop exceeding
3 percent at the farthest outlet of power, heating, and lighting
loads, or combinations of such loads, and where the
maximum total voltage drop on both feeders and branch
circuits to the farthest outlet does not exceed 5 percent,
provide reasonable efficiency of operation. See FPN No. 2
of 215.2(A)(3) for voltage drop on feeder conductors.
There is no receptacle load calc for resi, it is included in the general lighting load: commercial is 180 VA per receptacle/duplex or 360 for a quad per 220 14 (I) or maybe (K) 1VA per sq ft, depends.
laketime
ok thanks. The project is a marina and we are installing a quad outlet on every dock. So I guess I will use 360/quad
laketime
Can you break a run up in sections for voltage drop? Like if the full length of the run is 600' and calcs call for #4 wire, can you run #4 to a junction box and then lower wire size as you get closer to the end of the circuit or do you need to pull a #4 all the way to the end?
charlie b
Lockport, IL
Retired Electrical Engineer
Yes, you can calculate the VD in sections, with reduced conductor sizes as you get closer to the loads. But let me ask for a clarification. Marinas have their own rules, yes. But the rules have to do with the receptacles that serve the boats moored at the docks. Those are either rated 50 amps at 250 volts or 30 amps at 125 volts, and are not compatible with the standard 120 volt household power cords. The code gives relevant demand factors. But if you are talking about a general purpose receptacle on the dock, to be used for plugging in a drill or a fan or something, then I would calculate the VD using 360 VA for a quad.
Electric-Light
Speaking of such situation, what does the code say about the use of transformer right at the load panel?
A 120v 600' run with 4AWG has a drop of 4.5% @ 15A, 6%@20A
If you use 240v and use a 240-120 transformer, you can get away with 10AWG
240v 600' 10AWG @ 7.5A =4.5%, 10A=6% and 10AWG should be just fine for satisfying conductor overload protection requirement for 15A or 20A 240v breaker.
laketime
These are just general use receptacles not meant for shore power for boats.
Strife
Umm,
2400VA @ 80%?
If you're talking load calcs for demand, it doesn't matter unless it's for specific equipment.
In the first case it goes under the VA/sq ft, in the second, go back to the 2400VA @ 80%. I'm saying that because if you have a quad serving specific equipment, it'll be close to the max breaker.
Cow
Eastern Oregon
Can you set a subpanel or two closer to the receptacles?
Instead of running #4 to EVERY quadplex, can you run #2 to a 100 amp sub, then run #10-12's out to the receps? That would help voltage drop out a bunch and save quite a bit of money if it's feasible.
laketime
No.....how the design is...only need to run #4's to one dock the others ate #10's
iwire
Massachusetts
As this is an Article 555 installation and it sounds like you will be splicing a lot do not forgot 555.9
(The following are from the 2008 NEC)
555.9 Electrical Connections. Electrical connections shall
be located at least 305 mm (12 in.) above the deck of a
floating pier. Conductor splices, within approved junction
boxes, utilizing sealed wire connector systems listed and
identified for submersion shall be permitted where located
above the waterline but below the electrical datum field for
floating piers.
All electrical connections shall be located at least
305 mm (12 in.) above the deck of a fixed pier but not
below the electrical datum plane.
555.2 Definitions.
Electrical Datum Plane. The electrical datum plane is defined
as follows:
(1) In land areas subject to tidal fluctuation, the electrical
datum plane is a horizontal plane 606 mm (2 ft) above
the highest tide level for the area occurring under normal
circumstances, that is, highest high tide.
(2) In land areas not subject to tidal fluctuation, the electrical
above the highest water level for the area occurring
under normal circumstances.
(3) The electrical datum plane for floating piers and landing
stages that are (a) installed to permit rise and fall
response to water level, without lateral movement, and
(b) that are so equipped that they can rise to the datum
plane established for (1) or (2), is a horizontal plane
762 mm (30 in.) above the water level at the floating
pier or landing stage and a minimum of 305 mm
(12 in.) above the level of the deck.