I have an inspector that cites 110.26 for an area above a sub-panel in a mechanical room in a residential basement finish.
There is a 1/2" water pipe that runs across the ceiling fastened to the floor joists. There is also a furnace flue that is in the dedicated space as well. We kept all of the combustible material clear of that.
Now i'm confused as to the way the code reads on 110.26F(1)a and b.
(
It says that there can be no leak protection apparatus in the dedicated space in (a) then says it shall be permitted to be there if protection is provided in (b).
Trying not to move the panel if possible.
Sorry I should probably have posted this in NEC and don't know how to move it now.
There is a 1/2" water pipe that runs across the ceiling fastened to the floor joists. There is also a furnace flue that is in the dedicated space as well. We kept all of the combustible material clear of that.
Now i'm confused as to the way the code reads on 110.26F(1)a and b.
(
PHP:
1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d).
(a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone.
Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone.
(b) Foreign Systems. The area above the dedicated space required by 110.26(F)(1)(a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.
It says that there can be no leak protection apparatus in the dedicated space in (a) then says it shall be permitted to be there if protection is provided in (b).
Trying not to move the panel if possible.
Sorry I should probably have posted this in NEC and don't know how to move it now.