14 AWG Maximum Amp rating

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Why would the #14 amp change for that situation? If you are thinking because it is part of a rubber cord then T. 400.5(A) would probably take effect. There may be something else I don't know about..
 

dana1028

Senior Member
I think he's asking if this conductor is being used on a motor does his allowed amperage change [i.e. is he restricted by the 240.4 'small conductor' rule?].

If that is what is being asked, then - the 'small conductor' rule does not apply [so says 240.4(G)]....and you are allowed 20A on that conductor in a motor application.
 

ike5547

Senior Member
Location
Chico, CA
Occupation
Electrician
Is the control circuit "tapped from the load side of a motor branch-circuit short-circuit and ground-fault protective device(s)?"

Or some other arrangement?

Check out 430.72 and Table 430.72(B).

If you need to use column A of Table 430.72(B) it will lead you to 310.15, which will lead you right back to Table 310.16 and a maximum of 15 amps protection.

I think.
 