314.30(c)

Status
Not open for further replies.

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
I need a bunch of connectors for use in hand holes. Could you check page 2 of this link and tell me if you feel I could use either of these products? These is a considerable price difference.

Thanks as always.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Those connectors are made for underground splices. I have used them on low voltages wires. IMO, they are fine for a handhole.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
At first I didn't see where they were listed, but after zooming in I see they are.

UL Listed to 486D, 600 volts max. (1,000 Volts signs and fixtures)
 