Circuit Breaker Used as Switch

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Circuit breakers marked ‘‘HID’’ have been investigated for switching high intensity-discharge lighting loads on a regular basis at their rated voltage.

Circuit breakers marked ‘‘SWD’’ and rated 347 V or less are suitable for switching fluorescent lighting loads on a regular basis at their rated voltage.
 

kwired

Electron manager
Location
NE Nebraska
You will likely find that most common manufacturers have all their standard single pole 15, 20 and 30 amp breakers, and many will have even more than that rated for SWD. HID rating usually requires a specific model.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
You will likely find that most common manufacturers have all their standard single pole 15, 20 and 30 amp breakers, and many will have even more than that rated for SWD. HID rating usually requires a specific model.
I agree.
But, SWD rating is limited to 1 pole 15A and 20A breakers, with 120V and 277V being the common voltages.
 