Talked to a guy who bought an older home last year, he says that after a good rain that when they run the microwave or any other larger appliance that the lights will dim way down. But it only seems to do it after a good amount of rain. Could this be a ground rod issue having to do with the moisture in the ground?
The only way a grounding electrode system could ever cause symptoms such as this would be because some how it is being energized by the ungrounded conductor, and there is no fault path back to the transformer but through Earth, then the addition of rain in the earth could cause a lower impedance causing a high load on the service to the point the voltage drops off, but for this to occur there would have to be a few other problems including the lost of the path back to the source of the grounding system.
Other wise I have to agree with the others, have the POCO check for bad connections, also do a voltage check between the grounding and Earth, if there is voltage then you have other problems.
Be very carfull on these kind of calls you never know what you might find.