***Equipotential Bonding Lug (how to secure)***

Status
Not open for further replies.

dmagic281532

New member
Hi everyone. I have a quick question. I'm securing a metal railing to my Equipotential Bonding Grid. I'm doing this because the railing is metal and it's within 5' or less from my water source. My question is I'm using a solid copper bonding lug & securing it to my railing. What can I use to screw the lug down? This style of bonding lug just has a hole in it and a clamp only to tighten down the #8 wire. Is a metal self tapping screw sufficient? Any suggestions would be great! Thanks.

***In addition, I will be doing the same thing to my rain down spout.***
 
Last edited by a moderator:

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Drill and tap the post for a stainless machine screw?

On a dairy barn I did, the contractor would weld a rebar stub onto steel posts underground so I could put a ufer clamp on it. That worked really well...
 

tommyrice

Member
securing lug

securing lug

if rail is at least 1/16" thick,Fastenal sells 32 thread stainless steel self tapping screw.
 

tommyrice

Member
ss srew with copper lug

ss srew with copper lug

i don,t know if stainless and copper are compatable for this install.i usually use brass lay in lugs
 