Not always

Not always

We use VFDs all the time for conveyors and some have safety disconnects at the motor and some are before the drive. It depends on the customer. We rarely provide starters for overload protection or control with VFDs anymore. Again, only when the customer requires it.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Sorry guys what I meant is can there be a separate starter and a separate disconnect for a motor or would it always be a combo starter disconnect? Thanks.
 

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
We use VFDs all the time for conveyors and some have safety disconnects at the motor and some are before the drive. It depends on the customer. We rarely provide starters for overload protection or control with VFDs anymore. Again, only when the customer requires it.

Thanks.
 

Rick Christopherson

Senior Member
You don't normally have a motor starter or disconnect with a VFD (at least downstream from the VFD). This is because the VFD does not like it when the circuit is broken between the VFD and the motor. The VFD itself is the starter, and the disconnect should be upstream of the VFD where possible.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The code requires that you have a disconnect for the motor controller and for the motor itself. In this case the motor controller is the VFD and there must be a disconnect within sight from the VFD. The code also requires a disconnect within sight from the motor, but there are some exceptions that will permit the remote, lockable controller disconnect to be used in lieu of a disconnect within sight from the motor.
 

iwire

Moderator
Staff member
Location
Massachusetts
You don't normally have a motor starter or disconnect with a VFD (at least downstream from the VFD). This is because the VFD does not like it when the circuit is broken between the VFD and the motor. The VFD itself is the starter, and the disconnect should be upstream of the VFD where possible.

We work at one industrial location and they still place disconnects on the load side of VFDs but the disconnects are equipped with an auxiliary early break contacts that shut the VFD down if the disconnect is operated.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
So you can have a separate starter and a separate disconnect on a motor? THanks,

You can have ten separate starters and ten separate disconnects all in series on the same motor if you want. or you can have a single starter and disconnect in the same enclosure.

Think of a VFD as a fancy starter.
 