If a motor has a VFD would is also have a disconnect or starter? Thanks.
either is NEC acceptable
We use VFDs all the time for conveyors and some have safety disconnects at the motor and some are before the drive. It depends on the customer. We rarely provide starters for overload protection or control with VFDs anymore. Again, only when the customer requires it.
You don't normally have a motor starter or disconnect with a VFD (at least downstream from the VFD). This is because the VFD does not like it when the circuit is broken between the VFD and the motor. The VFD itself is the starter, and the disconnect should be upstream of the VFD where possible.
So you can have a separate starter and a separate disconnect on a motor? THanks,