armyofdone
New member
is it legal to have a ceiling drop of sjo end up in an UNMOUNTED metal 4x4 box. Basically just dangles there
No, 4"x4" square boxes are not allowed to be 'pendent' supported.
You need a box with a threaded hub.
314.23
Not exactly.maybe I did not read the OP correctly but the way I am reading it he has SJO cord in a approved manner and has a 4x4 Jbox at the other end ..So 314.23(H)1 box supported by cord would be allowed...
A 4x4 box does not have a hub. The hub must be a part of the box.(1) Flexible Cord. A box shall be supported from a multiconductor cord or cable in an approved manner that protects the conductors against strain, such as a strain-relief connector threaded into a box with a hub.
Not exactly.
"such as", "such as", Hmmmm, could there possibly be other approved means to protect the conductors against strain?
db
I don't got no PHD in English, or nothin', but, in my opinion, the words "such" and "as" in 314.23(H)(1) merely show the one example, but do not prohibit other methods of protecting the conductors against strain.
db
314.23(H) Pendant Boxes. An enclosure supported by a pendant
shall comply with 314.23(H)(1) or (H)(2).
Approved. Acceptable to the authority having jurisdiction.
Not exactly.
Or he can use a WP box with threaded ko's. And, of course seal off all unused ko's. And add strain relief.