Okay, let's start again. I am looking at two examples in Stallcup's "Electrical Calculations Simplified". Stallcup uses a method of calculating the neutral loads that I find confusing and inconsistent. Here is the first:
Office Building
120 Volt, Single Phase Loads
Office lighting load 525,000VA (before 125% factor applied)
Hall lighting load 1500VA (before 125% factor applied)
Track lighting load 4500VA
Outside lighting load 3600VA (before 125% factor applied)
Sign lighting load 4800VA
Noncontinuous Receptacle 68,760VA
Continuous Receptacle 21,780 (before 125% factor applied)
There are three-phase loads that are not applied to the calculation. I'm okay with that. This is how Stallcup performs the neutral load calculation:
Office Lighting Load 525,000VA
Hall Lighting Load 1,500VA
Total Load 526,500VA
Question: Why aren't the other 120 Volt loads used in the calculation? The track lighting, outside lighting, sign lighting, and receptacle lighting are not taken into account even though they are single phase loads that employ the neutral as a current carrying conductor. Why is this?
Office Building
120 Volt, Single Phase Loads
Office lighting load 525,000VA (before 125% factor applied)
Hall lighting load 1500VA (before 125% factor applied)
Track lighting load 4500VA
Outside lighting load 3600VA (before 125% factor applied)
Sign lighting load 4800VA
Noncontinuous Receptacle 68,760VA
Continuous Receptacle 21,780 (before 125% factor applied)
There are three-phase loads that are not applied to the calculation. I'm okay with that. This is how Stallcup performs the neutral load calculation:
Office Lighting Load 525,000VA
Hall Lighting Load 1,500VA
Total Load 526,500VA
Question: Why aren't the other 120 Volt loads used in the calculation? The track lighting, outside lighting, sign lighting, and receptacle lighting are not taken into account even though they are single phase loads that employ the neutral as a current carrying conductor. Why is this?