I have read numerous times, and verified, that SE cable must be installed based on the 60 degree rating.
I've installed a 3 meter base system, each meter having a 100amp main breaker to feed a panel of a 3 plex.
Does not Table 310.15(B)(6) (2008 NEC) allow the use of #2/3 w ground aluminum SE cable for this 100amp feed from the main to the interior panel (100 amp, 20 position)?
If not, please explain why.
I think it's OK, but hate to do things twice.
Thanks
I've installed a 3 meter base system, each meter having a 100amp main breaker to feed a panel of a 3 plex.
Does not Table 310.15(B)(6) (2008 NEC) allow the use of #2/3 w ground aluminum SE cable for this 100amp feed from the main to the interior panel (100 amp, 20 position)?
If not, please explain why.
I think it's OK, but hate to do things twice.