Gentlemen,
I am detailing a separately derived system power source where a single phase isolating 240:480 transformer is used to provide a feeder to another similar transformer 480:240/120 several hundred feet away (underground in HDPE conduit). I believe that I may run two conductors only (L1 and L2) between the two transformers provided that: I provide OCPD at each end of the run and provide a separate Ground at each end of the run with a separate EGC to each transformer and the enclosure containing the OCPD. I also need a Service Panel on the load side of the 240/120 transformer with appropriate OCPD and EGC to the same ground that ties to the transformer. Is all of this correct?
I am detailing a separately derived system power source where a single phase isolating 240:480 transformer is used to provide a feeder to another similar transformer 480:240/120 several hundred feet away (underground in HDPE conduit). I believe that I may run two conductors only (L1 and L2) between the two transformers provided that: I provide OCPD at each end of the run and provide a separate Ground at each end of the run with a separate EGC to each transformer and the enclosure containing the OCPD. I also need a Service Panel on the load side of the 240/120 transformer with appropriate OCPD and EGC to the same ground that ties to the transformer. Is all of this correct?