Considering the wording of 517.14;
how many interpret the last sentence to permit "daisy chaining" the #10 equipotential bonding conductor through the panels serving the patient care area?
Roger
517.14 Panelboard Bonding.
The equipment grounding terminal buses of the normal and essential branch-circuit panelboards serving the same individual patient care vicinity shall be connected together with an insulated continuous copper conductor not smaller than 10 AWG. Where two or more panelboards serving the same individual patient care vicinity are served from separate transfer switches on the emergency system, the equipment grounding terminal buses of those panelboards shall be connected together with an insulated continuous copper conductor not smaller than 10 AWG. This conductor shall be permitted to be broken in order to terminate on the equipment grounding terminal bus in each panelboard.
how many interpret the last sentence to permit "daisy chaining" the #10 equipotential bonding conductor through the panels serving the patient care area?
Roger
Last edited: