I have a commercial customer with metal conduit, metal receptacle box and an old two wire receptacle. It is my understanding that NEC agrees it is acceptable to replace the two wire receptacle with a GFCI receptacle or install a new three wire receptacle and use the metal box as a ground or is it best to pull a seperate ground wire?
 
IDK The customer wants me to replace it. It is on the rooftop where I use trouble light, vacuum pump ect and it is falling apart. If I did replace it, I would want to do it per code. Then can I replace the receptacle myself?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I have a commercial customer with metal conduit, metal receptacle box and an old two wire receptacle. It is my understanding that NEC agrees it is acceptable to replace the two wire receptacle with a GFCI receptacle or install a new three wire receptacle and use the metal box as a ground or is it best to pull a seperate ground wire?

If there's any doubt of the continuity of the conduit system from box to panel, It would be best to pull a separate EGC since it is in conduit. It would be easiest to just use the conduit if you can be sure it is a solid ground all the way.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I had done some research and found the OP to be a handyman. So............

I am closing this thread, in accordance with the Forum rules. This Forum is intended to assist professional electricians, inspectors, engineers, and other members of the electrical industry in the performance of their job-related tasks. However, if you are not an electrician or an electrical contractor, then we are not permitted to help you perform your own electrical installation work.


If I have misjudged the situation, if for example this project is related to your work, then send me a Private Message. If you can show me that I am wrong, and that you are a licensed electrician (or at least a licensed apprentice), then I will reopen your post, and offer an apology for the delay and inconvenience.

A reminder to all members, if you see a questionable post, feel free to report it by clicking the
report-40b.png
button at the bottom left corner of the post.
 
Status
Not open for further replies.
Top