PARALLEL RUNS
Alwayslearningelec
NJ
Estimator
Sorry guys I know I asked this but I was not clear. Why if you have say 4,5,6 parallel runs of 2".3" etc you can reduce the labor. What factors are taken into considerations that lessens the labor? THanks VERY MUCH
tkb
MA
You would be installing a rack for 2 or 6 would be the same labor, just more strut.
You would already be in the position to install one conduit. It doesn't take much more labor to install a second ot third.
You save labor because they share hangers and you work position doesn't change to add more conduits.
Also when you are pulling the wire, you setup once to pull multiple runs.
Most of the labor is saved with setup and common hangers.
sameguy
New York
Master Elec./JW retired
It is due to your feet stay in the same place for x# of repetitions, bend information is acquired faster.
a)The men move down the hall way one time installing x# of pipes.
b)The men move down the hall way x# of times installing 1 pipe.
Which a or b will get more work done faster?
Alwayslearningelec
NJ
Estimator
So are you saying there is a saving in wire pulling as well?? Thanks.
Alwayslearningelec
NJ
Estimator
A:roll:
tkb
MA
In the setup only. You still have the labor of pulling and termination.
It depends on how many pulls and the size of the reels and the way you recieve the cuts.