Is UL the only valid certification?

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Here is a list of the OSHA Nationally Recognized Testing Labs. Listing by any of these should be acceptable. The CE mark is not acceptable as that is a self certification, it does not require testing by an independent lab.
 

bphgravity

Senior Member
Location
Florida
NRTL's do not approve products rather they test, certifiy, & list products to the applicable recognized standard.

In the case of solar PV equipment, any of the NRTL's can test, certify & list the PV product to ANSI/UL 1703, for example.

Listing is one of the methods used to determine product approval by your local AHJ.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
It would be interesting to know of NJ's incentive programs have any restrictions such as only accepting UL listed equipment. I tried a little googling and couldn't find an answer.
 