We know that you can't run USE cable inside a building, but is there anything in the NEC that would disallow URD to be run to a meter socket in a residential application?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
depends on who installs it or has jurisdiction over it :D
really,,,
URD (with no other rating) is not a recognized conductor by the NEC (310.13)..
If the cable falls under NEC jurisdiction then it would not normally be approved...if the cable is under POCO jurisdiction, they can approve it.
 