knoppdude
Senior Member
- Location
- Sacramento,ca
Was asked this problem by an electrical project manager. Two 150 HP motors on the same starter, and breaker 800 amps. I told him that a 1/0 grounding conductor would have to be run to each motor per table 250-122. He said it did not make sense, and that he thought this could be reduced as the breaker was an instantaneous trip with adjustable settings. As I read section 250-122, there can be no reduction in the size of this equipment grounding conductor. Am I wrong, is there some part of article 430 that allows for a reduction? Section 250-122 seems to be very clear on this, and it makes sense that with two branch circuits on the same breaker, each would have to be capable of carrying the potential ground fault current, and as such should be sized using table 250-122. Thanks for all responses.