Installing a new 45kva transformer on the 4th floor of a hospital and there is no building steel or water pipe near. Can the sprinkler pipe be used?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Many sprinkler systems use a type coupling that actually isolates sections of the piping so they are useless as a ground plus Sprinkler Codes in many areas prohibit using them as a ground
 

jumper

Senior Member
Many sprinkler systems use a type coupling that actually isolates sections of the piping so they are useless as a ground plus Sprinkler Codes in many areas prohibit using them as a ground

I gave NFPA 13 a quick search, but I could find a prohibition, I think it is there somewhere: I just did not find it.:ashamed1:

I am most familiar with sprinkler head placement and hanger rules.
 

dkidd

Senior Member
Location
here
Occupation
PE
Many sprinkler systems use a type coupling that actually isolates sections of the piping so they are useless as a ground

Victaulic fittings are actually UL listed for bonding, so I don't know what fittings you are refering to.

As for water pipe, it is only permitted as a ground electrode if the grounding electrode conductor is connected within 5 feet of where the pipe enters the building
 