9-acre site in country, last house on poleline.
Site arrangement:
Transformer pole SE corner of house.
Coypond on E side of house.
House service middle of house on N side.
Garage20 ft NE of house.
Pool deck between back and E side of houseand W side of garage.
Pool pump panel on NW back of garage.
Pump panel feeder from house service point toSE of pool, 5ft from pool.
Pool is 15ft North of house and 10 ft W ofgarage.
Pond is 100ft N of garage.
Garage service from house service point to Wside of garage, 5 ft from pool.
Utility Service feeder is 7 ft south of pool.
In ground pool, E P Grid installed 9 sq"luminaire in contact with water, wet niche tied to EPG.
Problem:
Receiving voltage difference of 1 to 4 voltsbetween pool water and deck, only on garage and house side of pool. In coyfishpond 22 volt difference. Voltage changes with load energized. No voltagewithout load.
We have removed all branch conductors andadded a load bank at different points. No matter where the load is added to thehouse, garage or pump panel. As soon as a load is added voltages reoccur.
We have run a new OH service to the House. Voltageis still present.
Removing the feeder EGC at the pump panel novoltage. Against code.
Utility want to add Neutral blocker.
Anysuggestion on where to look.