feeder or branch circuit

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
No. A feeder must terminate in a overcurrent protective device per the Art 100 definition, and that has to be a listed disconnecting means, and the key rule is 225.36, the disconnecting means must be suitable for service equipment. This is a branch circuit with supplementary OCPD at each pole.
225.36 is not circuit specific. It applies to both feeders and branch circuits. In addition, there is the matter of location of the disconnecting means. For that, see 225.32 Exception No. 3.

On the other side of the coin, branch circuit tap conductors must meet the requirement of 210.19(A)(4) Exception No. 1, in which the big one is tap conductors not longer than 18" from the luminaire.
 

Smart $

Esteemed Member
Location
Ohio
In that case the OP would have to run same size conductors throughout the run.

RUWired I think you may be right.
#8 Cu 75?C or better is suitable for use on a 50A fused circuit provided it is not derated less than the next smaller standard fuse size and its ampacity is sufficient to carry the calculated load.

...So the #6's are upsized...
 
Last edited:

RUWired

Senior Member
Location
Pa.
#8 Cu 75?C or better is suitable for use on a 50A fused circuit provided it is not derated less than the next smaller standard fuse size and its ampacity is sufficient to carry the calculated load.

...So the #6's are upsized...

Your right again!!:cry:
 