I think I have this right, but my brain is fuzzy today, so here goes. I have a circuit ran in EMT between metal boxes, but in "smurf" (ENT) from first metal box to panel. The first box is only being used as a pull box, no splices or terminations. The second box has a receptacle mounted on a raised cover. I have a bonding jumper from the recep. to box. Since one box is bonded and connected to the other by the EMT, I wouldn't have to splice the EGC in the first box just to bond there with no other splices in that box. Do I have this right?
 

USMC1302

Senior Member
Location
NW Indiana
Bill, your wording is confusing me a little, but I'm probably fuzzy today too. What I think you are describing is a circuit from the panel to the first metal box in smurf tube and EMT from there down stream? The second metal box has a recept that you bonded to the box. Where is the EGC from the panel to the first box?
 

pete m.

Senior Member
Location
Ohio
I think I have this right, but my brain is fuzzy today, so here goes. I have a circuit ran in EMT between metal boxes, but in "smurf" (ENT) from first metal box to panel. The first box is only being used as a pull box, no splices or terminations. The second box has a receptacle mounted on a raised cover. I have a bonding jumper from the recep. to box. Since one box is bonded and connected to the other by the EMT, I wouldn't have to splice the EGC in the first box just to bond there with no other splices in that box. Do I have this right?

Sounds right to me.

Pete
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Bill, your wording is confusing me a little, but I'm probably fuzzy today too. What I think you are describing is a circuit from the panel to the first metal box in smurf tube and EMT from there down stream? The second metal box has a recept that you bonded to the box. Where is the EGC from the panel to the first box?

I told you my brain was fuzzy. I should have stated that I do have an EGC run with the ungrounded conductors. The first box is just a pull box, going straight through to the second box, where it is bonded to the box because of the cover mounted recep. That help clear it up some?