I got one for you.. I tried posting this in an existing thread, but nor responses..
We have a run that's about 800'. 225A/3P feeder at 208V.
The feeder is from a generator to a distribution panel at 535' away and than we continue one with the 2nd run at 265'.
The most significant load is a 13.6HP elevator. The mfg. recommends sizing feeder at 97 Amps which I assume is full load running. The other loads are some ventilation fans, EM lighting and other EM loads (dampers, etc.).
I calculate the connected load for the combined first and second loads at 190A, the 2nd run drops 15A - so we continue on with 175A.
I am proposing 2 sets of 600AL which is huge in the eyes of the contractor. I want to limit the drop to 3ish% because the 2nd feeder than continues on to secondary distribution panels and than on to branch circuits.
The elevator is used as a means of egress (re: 4 or more stories above grade, IBC..)
I am taking PF at 95% which I think is fair. The reality is that this may never draw the 190A, but I don't know if I'm being too conservative. Life safety makes me err to the conservative side.
Anyone have any input?
We have a run that's about 800'. 225A/3P feeder at 208V.
The feeder is from a generator to a distribution panel at 535' away and than we continue one with the 2nd run at 265'.
The most significant load is a 13.6HP elevator. The mfg. recommends sizing feeder at 97 Amps which I assume is full load running. The other loads are some ventilation fans, EM lighting and other EM loads (dampers, etc.).
I calculate the connected load for the combined first and second loads at 190A, the 2nd run drops 15A - so we continue on with 175A.
I am proposing 2 sets of 600AL which is huge in the eyes of the contractor. I want to limit the drop to 3ish% because the 2nd feeder than continues on to secondary distribution panels and than on to branch circuits.
The elevator is used as a means of egress (re: 4 or more stories above grade, IBC..)
I am taking PF at 95% which I think is fair. The reality is that this may never draw the 190A, but I don't know if I'm being too conservative. Life safety makes me err to the conservative side.
Anyone have any input?