Here is what I have: A large (800 kW) array on the roof with ballasted racking. The module frames and rails are bonded together and a #6 GEC is taking it down off the roof to a new auxillary DC GE. This ground will not be connected to the combiner boxes or the DC EGC. [690.43] [250.54] The Aux. GE will also not be connected to the existing GES because it is on the other side of the building.
The DC EGC then originates inside the combiner boxes (it is not electrically continual with the frames or rails) and is taken down to the inverter, where eventually it will share the same bonding point as the AC EGC, and DC GEC. The AC GE is not accessible and therefore I will be sharing the function of the AC EGC with the DC GEC. [690.47(C)]
If there were a fault in a PV Source Circuit to the frame/rail would there be a hazard? Wouldn't the fuse simply blow in the combiner because of the intentionally grounded circuit conductor?
I believe this is a code compliant method, what doesn't sit right with me is that there is no grounding between frames/rails and the combiner boxes.
The DC EGC then originates inside the combiner boxes (it is not electrically continual with the frames or rails) and is taken down to the inverter, where eventually it will share the same bonding point as the AC EGC, and DC GEC. The AC GE is not accessible and therefore I will be sharing the function of the AC EGC with the DC GEC. [690.47(C)]
If there were a fault in a PV Source Circuit to the frame/rail would there be a hazard? Wouldn't the fuse simply blow in the combiner because of the intentionally grounded circuit conductor?
I believe this is a code compliant method, what doesn't sit right with me is that there is no grounding between frames/rails and the combiner boxes.