That's a loaded question Ron!
In order for the primary device to coordinate with the secondary main, I can't get lower than the 2 second delay. Of course that's totally dependent on the adjustments to the secondary main that I've selected.
I based those adjustments on allowance of the breaker to tolerate an inrush from about 1800 kVA of small dry-type K-13 transformers that get picked up upon energization, which was from an actual power study I did recently.
That particular job had two 3750 kVA transformers with 480 Volt secondaries. One was loaded up with the 1800 kVA of dry-type transformers, and the other had two large VFD-driven motors, at around 1500 HP of load. The secondary of the one with dry-type xf loads did the 2-second timeout with the primary device, resulting from breaker adjustments to allow the inrush, with a resultant HRC Dangerous. The VFD/motors xf secondary had very little inrush, and the ocpd's were adjusted to minimize the incident energy level, resulting in a Hazard Risk Category 2.
The arc-flash advantage that MV systems have over LV systems is a direct result of the magnitude of the arcing fault current. LV systems have af currents on the order of 55% of the bolted fault current level, whereas the MV systems acring fault current is closer to 95% of the bolted fault current, resulting in much faster operation of the protective device.
John M