Thank you for the link.
But if a jurisdiction doesn't have amendments then the NEC is silent on this?
No, it is then up to the AHJ to determine "subject to physical damage". It becomes more subjective.
334.15(B) Protection from Physical Damage. Cable shall be
protected from physical damage where necessary by rigid
metal conduit, intermediate metal conduit, electrical metallic
tubing, Schedule 80 PVC conduit, or other approved
means. Where passing through a floor, the cable shall be
enclosed in rigid metal conduit, intermediate metal conduit,
electrical metallic tubing, Schedule 80 PVC conduit, or
other approved means extending at least 150 mm (6 in.)
above the floor.