Wire size for heater

Status
Not open for further replies.

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Hey just curious as to what others think?
what size wire (Cu) is minimum requirement for a 4,000 watt wall heater. No derating issue for voltage drop.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Just as I thought! 30 amp minimum wire ampacity and standard breaker size. I was asking because where I work mostly we use electric for heating. TIme and time again I see 4,000 watt cadet heaters on a 20 amp circuit. Sometimes I see melted connections.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Just as I thought! 30 amp minimum wire ampacity and standard breaker size. I was asking because where I work mostly we use electric for heating. TIme and time again I see 4,000 watt cadet heaters on a 20 amp circuit. Sometimes I see melted connections.

4000/240=16.7 amps.

It should work fine on 20A circuits without melting the connections. If you are melting a #12 wire with under 17A load, there is something else wrong.

I agree it should be sized as a continuous load so it can't legally be on a 20A circuit.
 