I've read through several posts about this but couldn't find a good reason as to why this is even used. In 2001, the company installed a Delta Delta 13.8/480. Later grounded the B phase. No problems encountered. One of the buss ducts it fed had all the equipment grounded with ground rods. That same ground from the B phase is ran to the buss duct as well. If I wanted to remove the corner ground, what type of problems should I expect if any. And the main question is, WHY have a corner grounded Delta to begin with?
I noticed the way you mentioned that the buss duct was grounded by ground rods, first I want to explain that grounding electrodes do not provide a low impedance path for fault current, nor are they allowed to, without having a low impedance path a fault to a grounded piece of equipment would not cause a breaker or fuse to operate to protect a person from a shock hazard, having a phase or a center tap such as in a WYE bonded to all equipment grounds provides a low impedance path back to source, Electricity does not want to flow to Earth, it wants to return back to source, this maybe a transformer or generator, or other means of supply but not Earth.
Now there are ungrounded systems allowed in certain circumstances but not without a phase monitoring system in place, these are allowed only where having the system go down would provide more of a danger then having a phase go to ground, this is to provide redundancy so the first fault goes to ground and sounds an alarm to allow time to schedule a shut down to repair it without taking the whole system down, it also only creates a grounded system on the first fault, the second fault will still take out the OCPD.