Suspended strip fixture with em and normal power

Status
Not open for further replies.

shaw0486

Senior Member
Location
baltimore
Good afternoon everyone,
I am working on a project that has alot of suspended strip fixtures that are numerous lengths. However there are 4' sections of these fixtures being fed with and EM circuit. Do you feel that this installation would comply with 700.9(B)(2) would it be acceptable to pull the em circuit and the normal through the fixture together? Or will i need to feed each section independantly so that the wiring is not ran together.
 

Attachments

  • Capture.PNG
    Capture.PNG
    5.3 KB · Views: 0

iwire

Moderator
Staff member
Location
Massachusetts
Do you feel that this installation would comply with 700.9(B)(2) would it be acceptable to pull the em circuit and the normal through the fixture together?

Nope.

Or will i need to feed each section independantly so that the wiring is not ran together.

We typically run EMT or MC cable on the top side of the fixtures if the fixtures are hanging down.
 
Status
Not open for further replies.
Top